Thread: Hot on the trail!

  1. #1
    Kennedy Guest

    Post

    OK, it won't be long now and I should actually get to USE my dyno! It's only been ready since Dec 24th (yes I broke my biggest and best toy Xmas eve) but I've been fighting electrical gremlins ever since.


    Last night I had it operating smoothly in the static load test (no vehicle) which is something I haven't been able to do on wall current. Generator yes, wall current no. Basically, if I switched off a particular circuit in the house which feeds from the same service as the dyno, it would work. I found that by switching the feed to the house off and on, I could shift the point at which things went wacky and could repeat the shifts pretty much at will.

    If I shut the main breaker off in the house panel, itgets better, but if I shut the feed to the house off at the other panel (essentially eliminating 100' of dead end line, it gets worse... Anybody with specialized knowledge in line current harmonics etc ?

  2. #2
    Join Date
    Jun 2000
    Location
    Arlington,MA U.S.
    Posts
    1,666

    Post

    How is your service laid out?
    Main panel in house, how many amp?
    subfeed to garage from there?
    Garage have it's own service?
    1998 6.5 2500 4X4 dynatrac pro 60, ARB, 35"BFG's
    06 D Max Express 5"MBRP EFI live

  3. #3
    Kennedy Guest

    Post

    Joey,

    I'd prefer not to consume bandwidth here, so I'll drop you a line.

    Suffice to say, it's looking like either:

    1) weak neutral

    2) Harmonics/resonance

    3) ground issues


    Thinking we may be trying an isolation transformer, as the harmonics thing seems to be prevailing thought. Switching different lines on and off seem to affect operation.

    My boiler's draft fan (solid state) also surges even though there is no call for heat when the dyno load changes...


    On edit: This thing has been consuming my life for nearly 2 months. At this point, the best solution that I see is to call in an industrial electrician to come in and evaluate the situation and try to measure what is going on when this is in operation. That way HOPEFULLY a finger can be pointed one way or another...

    [ 02-16-2004, 01:09 PM: Message edited by: kennedy ]

  4. #4
    LanduytG Guest

    Post

    John
    Someteimes the power company will get involed in cases like this. It might be worth asking. A good commercial electrition should be able to help as well.

    Gerg

  5. #5
    Join Date
    Apr 2003
    Location
    Tomah ,WI
    Posts
    85

    Post

    A proper grounding system requires two ground rods eight feet in length ,located a distance apart (6 ft.)?.I have also been told not to put them under the overhang of the roof,they get better contact in moist soil.As Greg said,contact your power company.I am on COOPERTIVE lines and they are helpful in situations like yours.
    2002 GMC D/A ext. cab,built 01-02

  6. #6
    Join Date
    Jan 2001
    Location
    Powhatan, VA
    Posts
    214

    Post

    I doubt the electric company will be much help unless you have a tremendous electric bill. Have you checked for voltage drop? Or something wired incorrectly. After years of living in my house, I found a wire on a receptacle wired to the wrong terminal and everything down from that was backwards. You could even have a loose connection somewhere. This can cause all sorts of wacky problems. Especially since many outlets and such are feed through and you could have a problem anywhere along the line. A partial connection somewhere can be fine until a load is put on it. Have you tried coming straight from the panel to eliminate a wiring issue? It could even be a breaker going bad.

    I would think a bad ground could be the culprit. I doubt harmonics. Harmonics have to be generated somewhere and are usually only a problem when they get to be a certain percentage of the load. I don't think the power company would be giving you that bad of a problem. If you switched off your other items such as computers that have switching power supplies and contribute to the harmonics, then I don't think this would be a problem. If your dyno is generating harmonics, it would most likely be a bigger problem on the generator unless you have some humongous generator.

    It could be in the dyno itself. Does it convert AC to DC to operate? It could be a power supply issue. I would contact the manufacturer and see if they have a recommendation.

    I would check for voltage drop. Since you said you were ok on a static test, the increased load may cause the problem. Check the incoming voltage with no load and with a load.

    Of course, you didn't mention anything about specs of the dyno. I'm not a dyno expert. Is it single phase, three phase, voltage, current draw, etc.

    Good Luck!!

  7. #7
    Kennedy Guest

    Post

    Quick overview:

    Single phase service.

    Panel A Bldg 1 200amp main feed Ground tested 25 ohms to ground. Neutral bonded to ground.

    Panel B Bldg 2 (New bldg with dyno) 100amp fed from panel A. 4 wire system, neutral/ground seperate. I added a ground rod at the dyno driven through the sump basin as an added ground source.

    Panel C 60amp (residence) fed from panel B. 4 wire system, neutral/ground seperate. I understand that by code, I need a ground rod for this building which I am lacking.


    Superflow has been here, and logged approx 30 hrs on this case.

    Power Co has set recorders, but see nothing outstanding. We never even exceeded 66 amps at peak draw. Planning to set another recorder again today. Power Co ends it's troubleshooting when it is determined that they are providing proper volts and amps.

    Dyno converts AC to DC to field the absorbers. First issue was blowing breaker. Found to be shorting the diode bridge to ground. Fought this for quite a while, and finally have a controller that works, but absorber "warbles" at a certain percentage of load. I can shift the point at which this occurs around pretty consistently.
    I have found that by turning the feed to the house off/on, I can alter shift the problem zone, AND if I shut down most/all of the house load on one particular leg, I can now get it to load smoothly top to bottom. Even with panel C main switched off, I can affect the point of trouble by switching the feed off and on. Better with lines connected than not.


    Tried to swap in replacement controllers (supposedly tested at SF) and BOTH blew breakers again, so back to the one controller that was working.

    Generator will run the unit without issue. Bear in mind I am only working with one contraooler and one absorber until we get SOMETHING to work.

    Fit to be tied...

    [ 02-17-2004, 09:49 AM: Message edited by: kennedy ]

  8. #8
    Join Date
    Apr 2003
    Location
    Encinitas CA
    Posts
    57

    Post

    The obvious may have already been tried, but have you "borrowed" a load isolation transformer and stuck it in after the generator/main power switch?
    \'01 Dmax/Ally Xcab LB, Amisoil air filter, Rancho shocks, \"Juiced\", Line-X, Westin tubes, \'02 Jayco 243RK fiver.

  9. #9
    Kennedy Guest

    Post

    Sneaks,

    That has been a common suggestion. I've been torn between buying one, or paying to have system tested.

    At this point I figure I'll have system tested if I can get a tech out here soon. That way I know where to send the bill...

    May prove to be my problem, but you never know. System requirements are stated at 220-240v 40 amps service at 60hz.

  10. #10
    Join Date
    Mar 2003
    Location
    Maine
    Posts
    13

    Post

    John'
    You might want to check and see how your neutral was connected in the sub panel if that is where you are making your connection. Normally sub panels do not ground the neutral. If the sub panel neutral is grounded you could have a ground loop problem. Should be easy to try it both ways. Grounding and neutrals is not something the local power company crews are very knowledgable about.
    Earl
    2003 Silverado SB/EC Dark Green
    Duramax/Allison, XM-Radio, Z82,VYU, DPF, UO1, UY2, and NP1. Bed mat, running boards,and 5th-wheel hitch.

  11. #11
    Kennedy Guest

    Post

    More detail edited into my system overview post.

  12. #12
    Join Date
    Jan 2001
    Location
    Powhatan, VA
    Posts
    214

    Post

    At what panel is the power company testing? All three? If not have you checked the voltage at each panel and at the point of power to the dyno?

    Did breaker trip instantaneously or after a period of time.

    Panel a feeding panel b with a 100 amp circuit--but is this the size of the breaker feeding the dyno?

    Sounds like you have an inrush/surge problem. Just because it is a 40 amp circuit, doesn't mean it can handle the inrush. How big is the breaker on your generator? Wire size and distance between panels could be a consideration as well.If your voltage is low, it could be causing the problem.

    I don't think ground loops would cause it to trip out on start up, unless you have a short somewhere, but they can definitely cause problems while running.

    Another thought is that when you are switching the panels on and off, you are not switching the neutral or ground, so they are still in play.

    I would check the voltage, breaker size and isolate the system and try it.--disconnect the neutrals and grounds going elsewhere. This is basically what you are doing when running on the generator.

    You may want to check and see if the power supply in the dyno is a switching type or linear.

    If you get to the point you think you need an isolation transformer or want to try something else, let me know what you are looking for. I might be able to help you out on the price. At this point, I just don't think thats its though.

  13. #13
    Kennedy Guest

    Post

    It gets pretty complicated, but basically, we have 2 large power absorber units aka eddy currents. They are DC powered by a control unit with a diode bridge/rectifier etc.

    We have basically ceased testing with vehicles, and gone to manually fielding one absorber in static state. The controller outputs DC voltage and varies amperage based on percentage of load ranging 0-15 amps over 0-100% load.

    The problem is, that when it "warbles" it is outputting too much amperage. The warble point can be shifted as stated above. When it clears the "warble, the output amperage gets back on track and things seem back to normal.

    Ex.

    50% output is approx 8 amps.
    55% warble 12 amps
    60% warble 12 amps
    65% clear 10.8 amps

  14. #14
    Join Date
    Apr 2003
    Location
    MN
    Posts
    82

    Post

    Is it possible to run the unit on 3-phase or 1-phase?

    If so, could it be wired for 3-phase but running on the single phase you are providing?

    Just thought I'd throw something out there. Sometimes the most obvious is the most overlooked. I see the specs are for 208-250VAC that's why I'm asking.
    2003 2500HD D/A, Ext. Cab, Sht Box<br />Lt. Pewter Metallic<br />265/75 Bridgestone Dueler REVO<br />Access Cover, Pendaliner<br /><b><a href=\"http://home.mchsi.com/~d.lang/2003_2500hd.htm\" target=\"_blank\">Some Pics</a></b>

  15. #15
    autocrosser Guest

    Post

    John,

    You should only ground your neutral at the main entrance panel. If I remember correctly you don't generate a second ground at the sub panel. You can generate more troubles by installing a second ground due to ground loops which will have current flowing on the ground lines.

    Also make sure that you haven't swapped grounds and neutral as it will function but not correctly.

    I don't know how you measured your ground resistance but it takes a special setup to do that properly such as a Biddle ground resistance tester and about 5oo' of wire that you string out to a stake and another long wire to probe the resistance along the path to find the lowest resistance. A ohm meter won't do it. You also have to isolate the system from the incomming power systems ground as it's a long path ground and won't be a good effective ground path due to the distance it travels to ground.

  16. #16
    Kennedy Guest

    Post

    Single phase machine on single phase power.

    Power Co checked ground with their gizmo and stated 25ohms.

    Ground/neutral ONLY bonded in first panel. Wire difference eliminates swapping potential.

    Looks like we'll definitely need tech out here to test everything power related.

    A suggestion to add capacitors to the feed lines has also been made. This is supposed to help clean up the line noise and is apparently what generators use.

    Again, Superflow was here for about 30hrs, and Power Co has checked out all of the obvious basics along with recording 24 hrs of VA readings.

    I will add that they tested Neutral by applying a 20 amp unblanaced load to either leg of the service. I watched this test, and saw the load leg go to 116ish, and non load go to 124ish from 120 normal. While in spec, it seemed kinda extreme for a 20amp load...

  17. #17
    Join Date
    Apr 2003
    Location
    MN
    Posts
    82

    Post

    Capacitors were another thought I had as well.

    We have a customer that uses extremely high DC voltages to produce a plasma that will melt down engine blocks and cars to a rock the size of a baseball. This AC-DC change causes some ugly harmonics and the capacitor idea has been thrown around to help that. We have them on a single feed with no other customers because of their particular situation.

    The changing of loads or opening up feeds to your home affecting the dyno is interesting/odd. If I understood correctly, with the mains open at the house breaker and just the line between the new shop and the house energized, it worked better?
    2003 2500HD D/A, Ext. Cab, Sht Box<br />Lt. Pewter Metallic<br />265/75 Bridgestone Dueler REVO<br />Access Cover, Pendaliner<br /><b><a href=\"http://home.mchsi.com/~d.lang/2003_2500hd.htm\" target=\"_blank\">Some Pics</a></b>

  18. #18
    Kennedy Guest

    Post

    I'm not sure how to take it, but switching different circuits on/off seems to be adding to the capacitance of the system???

    Switching things definitely causes changes, but sometimes the effect is different.

    Last night if I shut down the house, it ran fine. Last time I did this it warbled at 35% load.

    One thing consistent is my boiler in bldg A will flare (draft fan tries to start) when the load is stepped.

    Keep in mind we are manually fielding the load in 5% increments by pushing the load button on the controller.

  19. #19
    Kennedy Guest

    Post

    I spoke with the troubleshhoter from the Elctrician.

    He seems very sharp, and basically feels that it is nothing exotic, usually something simple etc etc.

    I have a pretty good feeling about this...

  20. #20
    Join Date
    Mar 2002
    Location
    Stillwater, Minnesota
    Posts
    404

    Post

    Minn-kota, are you talking about Northstar in Newport?

    John, did you get the optional tire drier? You'll get this thing all tuned up and ready to run and won't be able to pour the coals to it driving in with wet tires.